Yahoo Answers is shutting down on May 4th, 2021 (Eastern Time) and beginning April 20th, 2021 (Eastern Time) the Yahoo Answers website will be in read-only mode. There will be no changes to other Yahoo properties or services, or your Yahoo account. You can find more information about the Yahoo Answers shutdown and how to download your data on this help page.

Anonymous
Anonymous asked in Home & GardenDo It Yourself (DIY) · 9 years ago

What size wire for 30kw 3ph 230volt heat kit?

4 Answers

Relevance
  • 9 years ago
    Favorite Answer

    Calculate Amps (30,000 / 230) = 130.4 Amps

    1 ph to 3 ph (130.4 / 1.73) = 75.39 Amps

    HVAC 3 hour 125% (76 * 1.25) = 95 Amps

    #3 AWG CU THHN or

    #1 AWG AL THW

    Source(s): Local 46 Electrician
  • Jim W
    Lv 7
    9 years ago

    Whatever is wrong. Those figures would work for single phase not 3 phase. Go with the answer from the JW from 46.

  • Irv S
    Lv 7
    9 years ago

    Where are you that you have 3 Ph. 230V. Service??????

    For the more common 208V. 3 Ph. you'd need #2 AWG.

  • 9 years ago

    Figure 130-150 amps.

    That's 1/0 gauge.