Carrier HVAC prob with Honeywell thermostat?
I have a Carrier model FX4BNF030 and Honeywell RTH6350/6450 series programmable thermostat.
I can get the tstat to program and heat up the house, but it won't cool. It puts out heat when i select cool.
this is my original wiring when it was connected to the carrier tstat:
ORANGE - O/W2
RED - R
YELLOW - Y/Y2
GREEN - G
BLUE - C
WHITE - W/W1
My current wiring to the new honeywell is:
ORANGE - W2
GREEN - G
WHITE - W
YELLOW - Y
RED - R (JUMPERED TO RC)
BLUE - NOT CONNECTED
From what I interpreted from the installation guide, I understand that I am not to use the blue wire, so I didn't connect it.
I don't understand what type of system I have. I had an original problem months ago that turned out to have a 'shorted wire to ground' in the outside compressor unit. The tech that came told me that the tstat unit i was using ( a different honeywell tstat ) wouldn't work because i needed one that works for heat pumps, so i bought this unit, the one i'm having problems with. the tech connected the original carrier tstat back up and my head finally came on. i took that honeywell non heat pump tstat back to Lowe's and bought another honeywell that was designed for heatpump. while it worked for heat during the winter time, now i have no cooling, living in florida.
PLEASE HELP.
outside unit: PURON 38EYG024300
there is one long wire connection point board the top side is labeled conventional and the bottom is labeled heat pump.
conventional---------heat pump
blank-------------------------L
y2-----------------------------E
w2---------------------------aux
g--------------------------------g
w ---------------------------O/B
notused--------------notused
y-------------------------------y
r--------------------------------r
rc------------------------------rc
(R&RC jumpered)
the white wire is connected to w which is the same connection point as O/B
if i move the orange wire to where the white is, do i remove the white or leave it and short the orange and white wire together? What about the blue wire which is currently non-connected?
2 Answers
- JingoLv 410 years agoFavorite Answer
Oh ok, Using the labels on the bottom, Connect the orange wire to O/B. This provides power to the changeover valve. The changeover valve is what actually switches the unit from heat to cool.
The white wire should be on AUX.
Function 1 should be 5.
And actually Function 2 could be either 0 or 1 but I think 0 is correct for your unit. If this is reversed it will heat when it should cool and cool when it should heat.
The blue wire was a 24v common for power to the stat. Some thermostats will have a C terminal for that, some don't. Yours doesn't so cap it off, tape it off, cover it in a way that it won't touch anything.
Just for reference:
Y is the compressor. This will be on in heat and cool mode.
G is fan
Rc and Rh are 24 volt and should be jumpered as you have it.